LDC2250 defaulting to analog?
Please Log in or Create an account to join the conversation.
- roboteq
Please Log in or Create an account to join the conversation.
Please Log in or Create an account to join the conversation.
- Griffin Baker
Click on the mute button located to the left of the slider to disable the serial command.
Look at the top in the status led section to see if pulse radio turns on. If you are using a remote, make sure it is powered and all 3 of the pulse terminals are connected. Even if you aren\'t using channel 2, that still needs to be connected for some reason (from personal experience).
If pulse led comes on, you should be able to see the motors spin if you give it a command.
If you don\'t get the pulse radio led to come on try the following.
Make sure all 3 connectors to the RC are connected, B, Ch1, Ch2 to the receiver.
In the run tab on the top right, look at pulse inputs section. Do numbers show up in those fields and do they change as you move the throttle? If so, make sure both throttles are centered to home position.
Please Log in or Create an account to join the conversation.
Please Log in or Create an account to join the conversation.
- Griffin Baker
Please Log in or Create an account to join the conversation.
Please Log in or Create an account to join the conversation.
- Griffin Baker
Please Log in or Create an account to join the conversation.
I forgot. The LDC2250 should have a USB port already on it. You can connect to the pc using that.
Ur thinking the mdc2250, this one only has a single serial port
Please Log in or Create an account to join the conversation.
- Griffin Baker
You\'re right. I also had forgot that the USB gets removed in this product in the conversion.Griffin Baker wrote:
I forgot. The LDC2250 should have a USB port already on it. You can connect to the pc using that.
Ur thinking the mdc2250, this one only has a single serial port