Motor automatically runs when MagSensor PWM output is given to any pulse input
- avinash_sprw
- Topic Author
- Offline
Less
More
- Posts: 15
- Thank you received: 0
4 years 10 months ago - 4 years 10 months ago #29533712
by avinash_sprw
Motor automatically runs when MagSensor PWM output is given to any pulse input was created by avinash_sprw
I have MGS1600GY magnetic sensor and SDC2160 Motor Controller. I'm interfacing both using by using the multiPWM output from sensor and the pulseIn in the controller. The interfacing is fine and I get the expected results. Whenever the script in the motor controller is paused/not being run, motors are running automatically at full speed. This happens only when the PWM output from sensor is connected any pulseIn input in the controller. Any idea why its happening?
Please Log in or Create an account to join the conversation.
- avinash_sprw
- Topic Author
- Offline
Less
More
- Posts: 15
- Thank you received: 0
4 years 10 months ago - 4 years 10 months ago #29533713
by avinash_sprw
Replied by avinash_sprw on topic Motor automatically runs when MagSensor PWM output is given to any pulse input
Found out myself. In the configuration panel of Motor Controller PC Utility, Under Pulse Inputs, Pin1, Input Use was set to Motor Command. Now set to No Action
Please Log in or Create an account to join the conversation.
- Gabriel_Isko
4 years 10 months ago #29533717
by Gabriel_Isko
Replied by Gabriel_Isko on topic Motor automatically runs when MagSensor PWM output is given to any pulse input
Yes, that is what I was about to recommend checking. Glad you were able to resolve your issue.