Hyperterm output/Updating the controller
- pmartin
- Topic Author
18 years 2 months ago #3595360
by pmartin
Hyperterm output/Updating the controller was created by pmartin
I went through the update process and brought the controller up to v1.7b. When I turned it on with the Roboteq hyperterm configuration it printed the folling messages, not the standard startup one listed in the manual:
RoboEnc v1.0 04/17/04
03
:0000000000FF00009B9A06620000
:0000000000FF00009B9A06630000
:0000000000FF00009B9A06630000
:0000000000FF00009B9A06630000
:0000000000FF00009B9A06630000
:0000000000FF00009B9A06630000
:0000000000FF00009B9A06630000
.... it continues to print this until I dsiconnect. The Roborun utility shows that the update completed successfully, but this appears to be running v1.0! Are there changes that need to be made to the hyperterm config?
RoboEnc v1.0 04/17/04
03
:0000000000FF00009B9A06620000
:0000000000FF00009B9A06630000
:0000000000FF00009B9A06630000
:0000000000FF00009B9A06630000
:0000000000FF00009B9A06630000
:0000000000FF00009B9A06630000
:0000000000FF00009B9A06630000
.... it continues to print this until I dsiconnect. The Roborun utility shows that the update completed successfully, but this appears to be running v1.0! Are there changes that need to be made to the hyperterm config?
Please Log in or Create an account to join the conversation.
- cosma
18 years 2 months ago #3596410
by cosma
Replied by cosma on topic Re:Hyperterm output/Updating the controller
The continous string of data you see is normal.
It is the controller's internal parameters (temperature, amps, command, pwmout, ...) for data logging purposes.
It is automatically and continuously sent after power up when in RC or Analog mode.
To see the OK prompt only, you must operate the controller in RS232 mode.
You can do this either by configuring the controller in RS232 mode (using the PC utility) or by sending 10 consecutive "Cariage Return" characters while in RC or analog mode.
It is the controller's internal parameters (temperature, amps, command, pwmout, ...) for data logging purposes.
It is automatically and continuously sent after power up when in RC or Analog mode.
To see the OK prompt only, you must operate the controller in RS232 mode.
You can do this either by configuring the controller in RS232 mode (using the PC utility) or by sending 10 consecutive "Cariage Return" characters while in RC or analog mode.