Grounding
Note6: Beware not to create a path from the ground pins on the I/O connector and the battery’s minus terminal.
Is this a must? Or in high current applications needed but lower power levels it isn’t critical?
Basically we have a lot of other electronics running on the same system battery and some of those signals need to go into the HDC2450. Those signals obviously need a signal common but in this case that is the negative battery terminal.
I can get an isolated supply and run all the other telemetry off it but would rather not do that if I don\'t need to.
Thank you,
Mark
Please Log in or Create an account to join the conversation.
- roboteq
You just need to be careful.
On the power part, beware to never have the ground from the 15-pin connector wired to the - of the battery. If for any reason, the main ground wires get disconnected while high current is drawn, the return current will flow through the 15-pin connector ground. This will burn the wire and pin.
On the signal side, you must be careful that the radio, microcomputer, joystick or other doesnt get its ground directly from the battery. It should take the ground from the 15-pin connector. Otherwise, the serial/radio/analog signal will be extremely noisy to the point it will not work.
Please Log in or Create an account to join the conversation.
While the the - pole of the battery is connected to the GND pins of my LDC2250C, that is apparently not the same as the chassis, the metal plate of the motor controller.
When it is all working I measure the full power supply voltage (24 Volts) between the ground pin of the 15/9 pin connector and the metal plate.
At first I though my application of control lights to show the voltage was the cause, but when that is disconnected the same 24 volts is still between metal plate and the ground pins on the controller.
Is this a normal situation? Because the transceivers were grounded to their metal case, they received the full 24 volts on the ground and it burned out .
As it looks now I have to double isolate the controller so it does not touch any part of my - fully metal - system, something that is difficult to do and still has the chance of accidental short circuit.
Please advise, thanks.
Rob
Please Log in or Create an account to join the conversation.
- Griffin Baker
The bottom plate of the LDC2250 should be anodized and therefore should not make any connections to the gnd terminals.I have a similar problem that has resulted in 2 blown out RF transceivers because:
While the the - pole of the battery is connected to the GND pins of my LDC2250C, that is apparently not the same as the chassis, the metal plate of the motor controller.
When it is all working I measure the full power supply voltage (24 Volts) between the ground pin of the 15/9 pin connector and the metal plate.
At first I though my application of control lights to show the voltage was the cause, but when that is disconnected the same 24 volts is still between metal plate and the ground pins on the controller.
Is this a normal situation? Because the transceivers were grounded to their metal case, they received the full 24 volts on the ground and it burned out .
As it looks now I have to double isolate the controller so it does not touch any part of my - fully metal - system, something that is difficult to do and still has the chance of accidental short circuit.
Please advise, thanks.
Rob
Please Log in or Create an account to join the conversation.
there is room for improvement here.....
I have now isolated the whole unit from the chassis with plastic covered screws and velcro pads underneath the plate.
Still very sad that this - in my opinion not adequate - isolation has cost me almost more in RF-modules than the controller costs....
Otherwise, the system works well.
Please Log in or Create an account to join the conversation.
- roboteq
We have increased our vigilance regarding this question during manufacturing.