can open eds
5 years 8 months ago #29530603
by sebastian
can open eds was created by sebastian
we have a new mcd 2230 motor controller v3.2
and we are going to it with a plc via canopen.
our plc gives a error that it cannot establis a connection
the qeustion is if the ESD file is up to date for this motor controller
and we are going to it with a plc via canopen.
our plc gives a error that it cannot establis a connection
the qeustion is if the ESD file is up to date for this motor controller
Please Log in or Create an account to join the conversation.
5 years 8 months ago #29530607
by TechSupport
Replied by TechSupport on topic can open eds
The documentation has not changed at all. Are all of your protocols and settings matching? Our controllers run on the 115200 baud rate.
Please Log in or Create an account to join the conversation.
- roboteq
5 years 8 months ago #29530623
by roboteq
Replied by roboteq on topic can open eds
There are no known problems with the EDS.
Make sure that you do not use USB at all while using CAN. Use RS232 to conect to the PC.
You should see the CANOpen heartbeat as soon as it is enabled and running.
For troubleshooting CANOpen, it is best that you first use a CANOpen Monitor Tool. Then use SDO's to read/write objects as they are listed in the eds.
Note that TPDOs and RPDOs can only be used to transfer data from/to a set of internal variables. Microbasic scripting must then be used to assign these variables to a particular function. See manual.
Make sure that you do not use USB at all while using CAN. Use RS232 to conect to the PC.
You should see the CANOpen heartbeat as soon as it is enabled and running.
For troubleshooting CANOpen, it is best that you first use a CANOpen Monitor Tool. Then use SDO's to read/write objects as they are listed in the eds.
Note that TPDOs and RPDOs can only be used to transfer data from/to a set of internal variables. Microbasic scripting must then be used to assign these variables to a particular function. See manual.
Please Log in or Create an account to join the conversation.