What Dead Man Switch and Safety Stop does?

6 years 7 months ago - 6 years 7 months ago #29532682 by metRo_
Hello,

I have a SDC2130 and want to be able to stop the motor using the fastest way possible. I was looking around the manual and I want to know how Dead Man Switch and Safety Stop works.

I'm using a closed loop control.

If I set the command velocity to 0 or if I enable Dead Man Switch the resulting plots for velocity looks the same. One example using dead man switch and other setting velocity to 0 are shown below. Unfortunately I'm not at the lab right now so these are the only images I got with me.


Please Log in or Create an account to join the conversation.

6 years 7 months ago #29532693 by blake
Deadman Switch stops the motor(s) when the switch/condition is active but then resumes the same motor command as soon as the switch/condition is released.

Safety stop stops the motor(s) and the safety stop condition cannot be cleared until the motor command is brought back to zero.

Please Log in or Create an account to join the conversation.

6 years 7 months ago - 6 years 7 months ago #29532701 by metRo_
But how it stop the motor? Do it use the close loop control to stop the motor?

Please Log in or Create an account to join the conversation.