HDC2450 with NPC T64
12 years 1 month ago #29525579
by antiwong
HDC2450 with NPC T64 was created by antiwong
Hi,
I recently purchased a HDC2450 and 2 T64 motors. I have connected my HDC2450 to a 48VDC regulated voltage supply and i did configure the unit with the RoboRun+ program.
I did not change anything except for the following
1) Over Voltage Limit =24V
2) Amps Limit = 90A
3) PWM freq = 18kHz.
I am using open loop speed control.
I used the slider on the run tab in the program to move the motors but nothing is happening. Is there something i have set wrongly?
Please Help.
Anthony
I recently purchased a HDC2450 and 2 T64 motors. I have connected my HDC2450 to a 48VDC regulated voltage supply and i did configure the unit with the RoboRun+ program.
I did not change anything except for the following
1) Over Voltage Limit =24V
2) Amps Limit = 90A
3) PWM freq = 18kHz.
I am using open loop speed control.
I used the slider on the run tab in the program to move the motors but nothing is happening. Is there something i have set wrongly?
Please Help.
Anthony
Please Log in or Create an account to join the conversation.
12 years 1 month ago #29525581
by xxknxx
Replied by xxknxx on topic Re:HDC2450 with NPC T64
Wiring is ok? Is roborun detecting your HDC2450?
Please Log in or Create an account to join the conversation.
- roboteq
12 years 1 month ago #29525587
by roboteq
Replied by roboteq on topic Re:HDC2450 with NPC T64
If you set the overvoltage limit to 24V and apply 48V to the controller, it will go in Overvoltage and not run. You should see the OverVolt LED on in the run screen, however.
Please Log in or Create an account to join the conversation.
12 years 1 month ago #29525615
by antiwong
Replied by antiwong on topic Re:HDC2450 with NPC T64
Thanks everyone. Yes the problem was the over voltage. I set it to 50V and PWM ratio to 50%.
Is that right for this 24VDC motor? the input voltage is 48VDC.
Is that right for this 24VDC motor? the input voltage is 48VDC.
Please Log in or Create an account to join the conversation.
- roboteq
12 years 1 month ago #29525619
by roboteq
Replied by roboteq on topic Re:HDC2450 with NPC T64
If you want to keep the motor within its published voltage range, just put 50% in the Max Power Adjust configuration. This will effectively halve the max voltage the motor will be subjected to.
Please Log in or Create an account to join the conversation.