HBL2350 Hall Sequence and rotor direction problem
12 years 3 days ago #29526035
by jppedroni
HBL2350 Hall Sequence and rotor direction problem was created by jppedroni
Hello everyone,
I\'m working with a HBL2350 and a Faulhaber 4490 BLDC motor.
I configured the hall sensors sequence in order to get the one shown on Figure 39 (Advanced Digital Motor Controllers User Manual, v1.2, January 8, 2011).
I’m using Roborun+ rev 1.2 8/3/11. The problem is that when I send a positive command to the motor, the hall sensor count goes down instead of up!
I tried swapping two sensor wires with no luck.
Any help?
Regards,
Juan
I\'m working with a HBL2350 and a Faulhaber 4490 BLDC motor.
I configured the hall sensors sequence in order to get the one shown on Figure 39 (Advanced Digital Motor Controllers User Manual, v1.2, January 8, 2011).
I’m using Roborun+ rev 1.2 8/3/11. The problem is that when I send a positive command to the motor, the hall sensor count goes down instead of up!
I tried swapping two sensor wires with no luck.
Any help?
Regards,
Juan
Please Log in or Create an account to join the conversation.
- roboteq
12 years 3 days ago #29526037
by roboteq
Replied by roboteq on topic Re:HBL2350 Hall Sequence and rotor direction problem
This normally works. Try swapping another 2 hall sensor wires.
Please Log in or Create an account to join the conversation.
12 years 3 days ago #29526039
by jppedroni
Replied by jppedroni on topic Re:HBL2350 Hall Sequence and rotor direction problem
I\'ve tried the six hall permutations, each one with the same results. For each hall combination only one phase combination works. The thing is that when I get on my oscilloscope the hall sequence from Fig 39, with the rotor spinning, the Hall Sensor Counter indicator goes in opposite direction with respect to the command (That is, a ++ command makes the Hall Sensor Counter go -1, -2, -3... etc).
I\'m going to use an encoder to close the position loop. Will it work, despite the inverted Hall Sensor Counter?
Thanks,
J
I\'m going to use an encoder to close the position loop. Will it work, despite the inverted Hall Sensor Counter?
Thanks,
J
Please Log in or Create an account to join the conversation.
11 years 11 months ago #29526061
by jppedroni
Replied by jppedroni on topic Re:HBL2350 Hall Sequence and rotor direction problem
Good news, I closed the position loop with an encoder and everything works fine. Speed and direction from the hall sensors is still being informed with the wrong direction.