MDC2250 issues

12 years 3 days ago #29526496 by Anonymous
MDC2250 issues was created by Anonymous
I'm using an MDC2250 controller and I have 2 issues: 1. I'm controlling 2 motors by serial interface and is working well except that the gate is returning to the 0 position automatically. I'm controlling the motors in position closed loop. Is this normal? 2. When I activate the digital out pins nothing happens. I measure the voltage on them and is 0V even they are active or not. What should I have to check for those 2 outputs to work?

Please Log in or Create an account to join the conversation.

12 years 3 days ago #29526497 by Roboteq
Replied by Roboteq on topic RE: MDC2250 issues
For the first question, keep in mind that if you stop sending commands for more than 1s, a command of 0 will be assumed. In position mode, this means returning to position 0.
The outputs are open drain. So you need to put a load between the output and the + voltage.

Please Log in or Create an account to join the conversation.

12 years 3 days ago #29526498 by Anonymous
Replied by Anonymous on topic RE: MDC2250 issues
For the second issue I was thinking about the open drain but I asked just to be sure. For the first one the 1s time is related to the watchdog value? Is it correct?

Please Log in or Create an account to join the conversation.

12 years 3 days ago #29526499 by Roboteq
Replied by Roboteq on topic RE: MDC2250 issues
If you don't send a command every second or less, the watchdog will activate.
You can disable the watchdog by entering 0 in the configuration value. Or you can extend the timeout period from the current 1000ms to up to 32000ms

Please Log in or Create an account to join the conversation.