Can't read pulse inputs 5 and 6 on HDC2450
9 years 6 months ago #29528933
by lemma.r
Can't read pulse inputs 5 and 6 on HDC2450 was created by lemma.r
I can't get any value (other than 0) from pulse inputs 5 and 6 on a HDC2450.
Both the Pulse In fields in the Run tab of the Motor Control Utility and issuing ?PI or ?PIC in the Console tab result in a value of 0 for those 2 pulse inputs. The other 4 work fine. I re-plugged the outputs of the Futaba receiver so that those that were in 3 and 4 were now in 5 and 6 but I still get 0. According to the manual that means the pulse inputs are disabled but according to the Configuration tab they are all enabled. None of the multiple purpose functions of those input pins (ANA5, ANA6, DIN5, or DIN6) are enabled.
Do you have any suggestions as to what else I could try please?
Motor Control Utility Rev 1.2 1/4/14, HDC2450 firmware v1.2 RCB400 10/10/2013
Both the Pulse In fields in the Run tab of the Motor Control Utility and issuing ?PI or ?PIC in the Console tab result in a value of 0 for those 2 pulse inputs. The other 4 work fine. I re-plugged the outputs of the Futaba receiver so that those that were in 3 and 4 were now in 5 and 6 but I still get 0. According to the manual that means the pulse inputs are disabled but according to the Configuration tab they are all enabled. None of the multiple purpose functions of those input pins (ANA5, ANA6, DIN5, or DIN6) are enabled.
Do you have any suggestions as to what else I could try please?
Motor Control Utility Rev 1.2 1/4/14, HDC2450 firmware v1.2 RCB400 10/10/2013
Please Log in or Create an account to join the conversation.
- Griffin Baker
9 years 6 months ago #29528938
by Griffin Baker
Replied by Griffin Baker on topic Can't read pulse inputs 5 and 6 on HDC2450
You are correct, that they do not work. It would require a firmware change.
Please Log in or Create an account to join the conversation.
9 years 6 months ago #29528940
by lemma.r
Replied by lemma.r on topic Can't read pulse inputs 5 and 6 on HDC2450
Is a firmware update in the works to get those pulse inputs working?
Please Log in or Create an account to join the conversation.
- Griffin Baker
9 years 6 months ago #29528944
by Griffin Baker
Replied by Griffin Baker on topic Can't read pulse inputs 5 and 6 on HDC2450
As far as I know, not currently. Are these the only 2 pulse inputs you have to utilize?
You can use a working pulse input and then use the pulse inputs 5 and 6 for a different connection (analog input 5 Digital input 5, analog input 6 Digital input 6)
You can use a working pulse input and then use the pulse inputs 5 and 6 for a different connection (analog input 5 Digital input 5, analog input 6 Digital input 6)
Please Log in or Create an account to join the conversation.
- Griffin Baker
9 years 6 months ago #29528946
by Griffin Baker
Replied by Griffin Baker on topic Can't read pulse inputs 5 and 6 on HDC2450
If you need to have all 6 pulse inputs for your application, please contact us directly at This email address is being protected from spambots. You need JavaScript enabled to view it.
Thanks.
Thanks.