SDC2130 TO DELTA PLC
8 years 3 months ago #29530821
by tuncel
SDC2130 TO DELTA PLC was created by tuncel
hello everyone
i have a problem. i cant communication sdc2130 and delta sx2 plc how can i communicate with rs232
i have a problem. i cant communication sdc2130 and delta sx2 plc how can i communicate with rs232
Please Log in or Create an account to join the conversation.
8 years 3 months ago #29530822
by TechSupport
Replied by TechSupport on topic SDC2130 TO DELTA PLC
The controller uses pins 2 (tx), 3 (Rx), 5(GND). You PLC is wired differently, but that is fine.
What you will need to do is connect those wires back to the controllers I/O on the 15 pin connector to make it work. Make sure to also set up the correct communications settings.
115200 bits/s
8-bit data
1 Start bit
1 Stop bit
No Parity
What you will need to do is connect those wires back to the controllers I/O on the 15 pin connector to make it work. Make sure to also set up the correct communications settings.
115200 bits/s
8-bit data
1 Start bit
1 Stop bit
No Parity
The following user(s) said Thank You: tuncel