Resolver setup and test not referenced in manual
- ledhunden@hotmail.com
- Topic Author
- Offline
Less
More
- Posts: 1
- Thank you received: 0
4 years 1 month ago #29534542
by ledhunden@hotmail.com
Hello,
I have a new RGBL1896 which is supposed to run a BLDC-motor which uses a resolver as position feedback.
In the user manual (V1.8 ) I see resolver referenced a couple of times, but the part that describes the resolver calibration seems to be missing. Or are you supposed to use the same calibration sequence as for sin/cos sensor?
I need to know the correct way to calibrate the resolver feedback because as it is now, I don’t know if I am having issues with the resolver wiring or the calibration sequence.
Any help with describing the calibration steps for resolver would be greatly appreciated.
Best Regards,
Niklas
I have a new RGBL1896 which is supposed to run a BLDC-motor which uses a resolver as position feedback.
In the user manual (V1.8 ) I see resolver referenced a couple of times, but the part that describes the resolver calibration seems to be missing. Or are you supposed to use the same calibration sequence as for sin/cos sensor?
I need to know the correct way to calibrate the resolver feedback because as it is now, I don’t know if I am having issues with the resolver wiring or the calibration sequence.
Any help with describing the calibration steps for resolver would be greatly appreciated.
Best Regards,
Niklas
Please Log in or Create an account to join the conversation.
- Gabriel_Isko
4 years 3 weeks ago #29534559
by Gabriel_Isko
Replied by Gabriel_Isko on topic Resolver setup and test not referenced in manual
In the current release firmware it performs a calibration step when you switch to sinusoidal.
Can you post the resolver you are trying to use? It may draw too much current - we can only drive ~250mA on our RGBL1860 Resolver Excitation.
Can you post the resolver you are trying to use? It may draw too much current - we can only drive ~250mA on our RGBL1860 Resolver Excitation.